Without having completely read the 3 page PDF; it looks like that applies to fixed installations, not extension cords.
It also doesn't differentiate between a lot of different methods of installation.
For example. If we take the list of 18 to 8 AWG 3-wire loaded 90 degree cable, it lists these currents;
18
25
30
40
55
Compare that to what we have here for 3-wire 90 degree (C) cables, directly buried;
23
30
39
49
65
The current ratings from that document are very close (slightly above) for what we have for 'wire in conduit in thermal insulation'. Nowhere near applicable for having an exposed extension cord.
And still; those tables are for 3-wire loads, not simple 2-wire loads which would be the case in the question from [member=75204]jordanrossbell[/member] . The current rating would again increase ~17%
Eaton's 20A isolator switch doesn't even allow for 4mm^2 (12 gauge) wiring to be connected btw.
Michael Kellough said:
Coen said:
Michael Kellough said:
“Are American amps different?‘
No, but voltage is different.
1300 watts divided by 220 volts = ~ 6 amps, so a lightweight power cord is fine.
1300 watts divided by 110 volts = ~ 12 amps, so a heavier cord is needed.
Yes I know. I was taking on the list of [member=7493]Sparktrician[/member]
“We use 1.5mm^2 (=16 gauge) extension cords for everything up to and including 16A”
Wow [blink] 16 amps of 220volts is 3500 watts. Do you even have anything that pulls that much? A heater? Does the cord get hot when carrying that much current?
Cooktops, ovens, dish washers, boilers; lots of stuff that draws 16A perfectly fine over 1.5mm^2. The cord can get warm, but so what. Better than having this huge anaconda as an extension cord. Unless you have an insanely high % of utilization you are not gonna earn back the extra investment either. For solar panel installations it's different; you base it own return on investment. 4mm^2 cable often makes financial sense even if 1.5mm^2 would still be within limits.
Festool CTL's come with an 1.5mm^2 cord and have a 2400W rated outlet on them, per official Festool specs.