Hi. I have a 500 square foot shop(detached garage 100 amp service) that is divided into 2 parts. The back part of the shop (150 sf) is where my work benches are, and the front part is 350 sf. I have a 4 kilowatt heater and I am adding a 1500 watt electric baseboard heater to the the front part of the shop which will stay set to prevent freezing all the time and turned up for comfort when I am working out there.
My question is this:
Presently I have the 4 kilowatt heater installed in the front part of the shop with #10 nmd90 and a double pole 30 amp breaker. The run to this heater is approx. 30 feet. What I'd like to do is feed both heaters from the one 30 amp breaker. The baseboard heater is 1500 watts, and 220 volts as well.
So what I am thinking is a 30 foot run (pull back original feed in attic) to junction box with #10, 2 foot run to 4 kilowatt heater, and run another line from the JB to the baseboard heater in the back shop. I am also wondering if I could use a smaller gauge wire to feed the baseboard heater as it will only be drawing approx 7 amps( 15 foot run)....I only ask as I'll have to go buy another length of # 10 wire if I decide or need to feed the smaller heater. I have lots of #12 and #14 kicking around......
I realize I could do this if it was on it's own breaker with no issues as it's only drawing approx 7 amps.....just not sure what might happen in the JB with the 4 kilowatt heater pulling more amps and having smaller wire in a marrett also pulling to the baseboard heater......
I am more inclined to just get the number 10 wire and feel safer about it all, but need to know firstly if I can feed both heaters from one breaker....
The smaller electric baseboard heater is also rated to 30 amp max. I don't think I'm overfeeding the smaller heater should something happen the breaker should still kick......
I also realize I am right on the line for what I could be pulling from this breaker with both heaters on. While that may happen on occasion, I only heat the larger part on rare occasions.....but they could both be running at one time, so it needs to be safe.
I do have a bit of knowledge as I worked for a electrical contractor when I was younger, so know the basics and some code, just most of it's 20 year old knowledge.....lol
Thaniks for any and all help.
Greg.
My question is this:
Presently I have the 4 kilowatt heater installed in the front part of the shop with #10 nmd90 and a double pole 30 amp breaker. The run to this heater is approx. 30 feet. What I'd like to do is feed both heaters from the one 30 amp breaker. The baseboard heater is 1500 watts, and 220 volts as well.
So what I am thinking is a 30 foot run (pull back original feed in attic) to junction box with #10, 2 foot run to 4 kilowatt heater, and run another line from the JB to the baseboard heater in the back shop. I am also wondering if I could use a smaller gauge wire to feed the baseboard heater as it will only be drawing approx 7 amps( 15 foot run)....I only ask as I'll have to go buy another length of # 10 wire if I decide or need to feed the smaller heater. I have lots of #12 and #14 kicking around......
I realize I could do this if it was on it's own breaker with no issues as it's only drawing approx 7 amps.....just not sure what might happen in the JB with the 4 kilowatt heater pulling more amps and having smaller wire in a marrett also pulling to the baseboard heater......
I am more inclined to just get the number 10 wire and feel safer about it all, but need to know firstly if I can feed both heaters from one breaker....
The smaller electric baseboard heater is also rated to 30 amp max. I don't think I'm overfeeding the smaller heater should something happen the breaker should still kick......
I also realize I am right on the line for what I could be pulling from this breaker with both heaters on. While that may happen on occasion, I only heat the larger part on rare occasions.....but they could both be running at one time, so it needs to be safe.
I do have a bit of knowledge as I worked for a electrical contractor when I was younger, so know the basics and some code, just most of it's 20 year old knowledge.....lol
Thaniks for any and all help.
Greg.