luvmytoolz said:Mini Me said:I have been running a Leeson USA motor on 75hz for many years with no smoke escaping from it yet.
50Hz?
Yes, through a VFD
luvmytoolz said:Mini Me said:I have been running a Leeson USA motor on 75hz for many years with no smoke escaping from it yet.
50Hz?
keithwwalker said:Can any european tool owners check their Festool tracksaw (or other device) and see if there is a voltage range for their corded tool?
I think cordless tool chargers can take 120-240, to charge the battery, so that is not at issue, but I am just speculating.
alltracman78 said:It's next to impossible to find a direct UK 110 to US 120 or a UK 240 to US 240 plug adapter.
Coen said:The 110v UK plug is just a standard 110V IEC 60309 16A plug
I can find a boatload of these adapter cables. But you might just as well make them yourself. But if you keep the tool in the USA, just replace the plug and be done...
keithwwalker said:Great discussion, but let me be more specific, many electric tools have name plate data right on the tool that states that it will run on a range of voltages & frequencies. It usually something like:
110-230 VAC, 50-60Hz
Can any european tool owners check their Festool tracksaw (or other device) and see if there is a voltage range for their corded tool?
I think cordless tool chargers can take 120-240, to charge the battery, so that is not at issue, but I am just speculating.
alltracman78 said:Coen said:The 110v UK plug is just a standard 110V IEC 60309 16A plug
I can find a boatload of these adapter cables. But you might just as well make them yourself. But if you keep the tool in the USA, just replace the plug and be done...
Adapter cables to US 120 or 240?
Link please?
Coen said:Festool prices in the USA are inflated compared to Europe anyway, so he might not have lost any (significant) money by selling in the USA and buying new in Europe.
alltracman78 said:Coen said:The 110v UK plug is just a standard 110V IEC 60309 16A plug
I can find a boatload of these adapter cables. But you might just as well make them yourself. But if you keep the tool in the USA, just replace the plug and be done...
Adapter cables to US 120 or 240?
Link please?
NEMA 5-15 plug to IEC60309 110v 16A socket;https://toughleads.co.uk/products/american-nema-5-15-plug-to-cee-16a-110v-socket-adaptor
IEC60309 110v 16A plug to NEMA 5-15 socket;https://toughleads.co.uk/products/cee-16a-110v-plug-to-american-nema-5-15-socket-adaptor
But there is nothing magic about it. You can just make those yourself by taking an normal extension cord and replacing one end with the IEC60309 110v 16A plug / socket.
The same in 240V is probably harder to find... because who is taking their European appliances with them to the US when moving? But they too can be made. I don't really know what to search for anyway since the USA seems to have a near endless choice in different 240V outlets, but assuming you can buy separate plugs you might just as well fabricate the cable yourself.
But when importing from the UK for permant stay in the USA; just cut off the UK plug and replace with your US equivalent.
Coen said:It's done because it's a requirement.
They already have enough people hurting their feet on their version of 230V plug that always ends up pins up on the floor that they had to mandate 110V on building sites to save a few life years there.
Crazyraceguy said:[member=79208]alltracman78[/member] I would certainly hope that guys who go back and forth between the shop and job-site would just use 110V and be done with it. Even if there was some tool that you had multiples of, it would seem to me that being able to use any of them on site would be advantageous.
Like if you had a TS55 that you used in the shop and a second one for site work in a van, but something happened to the site saw (dropped and bent the base, switch went bad, etc) the other saw is still usable on site. If you had a 240V one for the shop, you're stuck until repairs can be made. For a professional, that's a no go.
Crazyraceguy said:Coen said:It's done because it's a requirement.
They already have enough people hurting their feet on their version of 230V plug that always ends up pins up on the floor that they had to mandate 110V on building sites to save a few life years there.
Is that seriously the reason? No way? If foot injury really is a thing, it seems like there are far easier ways to overcome that than a voltage change, simply because the plugs are different?
Crazyraceguy said:I honestly don't know what would happen here if you showed up on a job-site with a step-up transformer and a 240V tool? I assume that someone would blow a gasket and throw you out, but I'm not sure of it? [huh]
alltracman78 said:UK Spec HK 85
View attachment 1
https://www.amazon.com/Universal-110-250V-American-Electrical-converter/dp/B07FKLLW2Walltracman78 said:Coen said:Festool prices in the USA are inflated compared to Europe anyway, so he might not have lost any (significant) money by selling in the USA and buying new in Europe.
alltracman78 said:Coen said:The 110v UK plug is just a standard 110V IEC 60309 16A plug
I can find a boatload of these adapter cables. But you might just as well make them yourself. But if you keep the tool in the USA, just replace the plug and be done...
Adapter cables to US 120 or 240?
Link please?
NEMA 5-15 plug to IEC60309 110v 16A socket;https://toughleads.co.uk/products/american-nema-5-15-plug-to-cee-16a-110v-socket-adaptor
IEC60309 110v 16A plug to NEMA 5-15 socket;https://toughleads.co.uk/products/cee-16a-110v-plug-to-american-nema-5-15-socket-adaptor
But there is nothing magic about it. You can just make those yourself by taking an normal extension cord and replacing one end with the IEC60309 110v 16A plug / socket.
The same in 240V is probably harder to find... because who is taking their European appliances with them to the US when moving? But they too can be made. I don't really know what to search for anyway since the USA seems to have a near endless choice in different 240V outlets, but assuming you can buy separate plugs you might just as well fabricate the cable yourself.
But when importing from the UK for permant stay in the USA; just cut off the UK plug and replace with your US equivalent.
Funny, the connector that's more niche ( UK 120 volt ) is easier to find than the more common UK 240 volt.
I hate cutting plugs if I can help it (OCD thing); I made an adapter cord for mine. But yes, very easy to cut the cord and wire a new plug on the end.
NEMA 6-15 is the US 240 volt 15 amp connector ( P on the end for plug, R on the end for receptacle).
NEMA 6-20 is the US 240 volt 20 amp connector.
The 6-15P will plug into the 6-20R and is allowed to be used in it.
The 6-20 won't plug into the 6-15 for obvious reasons.
You want one of those 2; the other 240 volt connectors are rated for ( and can carry) higher current, which if you have a short can cause a big problem.
IIRC there is also a 15 and a 20 amp twist lock connector for 240 volts FYI.
*Looked it up so there wouldn't be any confusion.
NEMA L6-15 is the 15 amp locking connector
NEMA L6-20 is the 20 amp locking connector.
In this case the 6-15 will not plug into the 6-20.*
alltracman78 said:Thinking about this UK 120 volt "requirement" has me thinking though. I wonder if there's more 120 volt tools over there than 240 volt ones? What percentage of the tools are used on jobsites vs at home? What's considered a jobsite? I would assume building a new house would be? What about renovations? Do professionals with a home workshop use 120 in their workshop? Or do they have different tools for jobsite vs home/customer site work?
Crazyraceguy said:[member=8955]Coen[/member] it's the same way here. The wires are just stapled to the studs inside the walls and quite destructive to access.
In commercial buildings it's a combination of both. In the office spaces with regular walls, it's the same as residential. In open shop/warehouse type spaces it's all in conduit, metal or PVC. I'm certainly not an electrical expert, knowing just enough to get by.
squall_line said:Crazyraceguy said:[member=8955]Coen[/member] it's the same way here. The wires are just stapled to the studs inside the walls and quite destructive to access.
In commercial buildings it's a combination of both. In the office spaces with regular walls, it's the same as residential. In open shop/warehouse type spaces it's all in conduit, metal or PVC. I'm certainly not an electrical expert, knowing just enough to get by.
Unless you're in the city of Chicago, where they have their own addendum to the NEC that requires conduit in residential. A significant number of the suburbs adopted that as well. The box stores still seem to sell quite a bit of NM / Romex cable. Fancy that...
Coen said:alltracman78 said:UK Spec HK 85
View attachment 1
The older ones say 2300W [tongue]
https://www.amazon.com/Universal-110-250V-American-Electrical-converter/dp/B07FKLLW2WCoen said:Coen said:Festool prices in the USA are inflated compared to Europe anyway, so he might not have lost any (significant) money by selling in the USA and buying new in Europe.
alltracman78 said:Coen said:The 110v UK plug is just a standard 110V IEC 60309 16A plug
I can find a boatload of these adapter cables. But you might just as well make them yourself. But if you keep the tool in the USA, just replace the plug and be done...
Adapter cables to US 120 or 240?
Link please?
NEMA 5-15 plug to IEC60309 110v 16A socket;https://toughleads.co.uk/products/american-nema-5-15-plug-to-cee-16a-110v-socket-adaptor
IEC60309 110v 16A plug to NEMA 5-15 socket;https://toughleads.co.uk/products/cee-16a-110v-plug-to-american-nema-5-15-socket-adaptor
But there is nothing magic about it. You can just make those yourself by taking an normal extension cord and replacing one end with the IEC60309 110v 16A plug / socket.
The same in 240V is probably harder to find... because who is taking their European appliances with them to the US when moving? But they too can be made. I don't really know what to search for anyway since the USA seems to have a near endless choice in different 240V outlets, but assuming you can buy separate plugs you might just as well fabricate the cable yourself.
But when importing from the UK for permant stay in the USA; just cut off the UK plug and replace with your US equivalent.
Funny, the connector that's more niche ( UK 120 volt ) is easier to find than the more common UK 240 volt.
I hate cutting plugs if I can help it (OCD thing); I made an adapter cord for mine. But yes, very easy to cut the cord and wire a new plug on the end.
NEMA 6-15 is the US 240 volt 15 amp connector ( P on the end for plug, R on the end for receptacle).
NEMA 6-20 is the US 240 volt 20 amp connector.
The 6-15P will plug into the 6-20R and is allowed to be used in it.
The 6-20 won't plug into the 6-15 for obvious reasons.
You want one of those 2; the other 240 volt connectors are rated for ( and can carry) higher current, which if you have a short can cause a big problem.
IIRC there is also a 15 and a 20 amp twist lock connector for 240 volts FYI.
*Looked it up so there wouldn't be any confusion.
NEMA L6-15 is the 15 amp locking connector
NEMA L6-20 is the 20 amp locking connector.
In this case the 6-15 will not plug into the 6-20.*
alltracman78 said:Thinking about this UK 120 volt "requirement" has me thinking though. I wonder if there's more 120 volt tools over there than 240 volt ones? What percentage of the tools are used on jobsites vs at home? What's considered a jobsite? I would assume building a new house would be? What about renovations? Do professionals with a home workshop use 120 in their workshop? Or do they have different tools for jobsite vs home/customer site work?
alltracman78 said:I sense some hostility towards the UK there. [laughing]