Steve Hiscocks said:
Hi, i have resently bit the bullet and perchased a kapex ( just dont tell the wife what it cost), my problem is, when running of the ct22 itseams to run a bit slow, blade speed that is. I looked at the specs of the ct to see if iwas over loading it. To my horror i found the rating for the plug on the ct is only 300 watt on the 110v GB model. Yet i have running my ts55 for years with no problems for that matter the of 1400 has never given me a problem.( I am using a 3kva transformer) does anyone have any ideas to whyits running slow or for that matter why the ct has such a low rating when the 240v Gb and the 110v US model has a rating of over 2000 watt.
a 3kw dry type transformer is more than enough to run that combo.
when you overload a transformer, the core won't carry enough flux to maintain the output...
here's how to tell what gives.... stick a digital voltmeter in the plug next to the one the vac
is using, best if you have one with a min/max capture, and cut a 4x4 or something significant,
and see what the voltage dips to.
i'd be willing to bet a cheeseburger that voltage on the secondary side of the xfmr won't dip.
it'll dip when you start the saw, 'cause of the inrush current, but when cutting, i bet it doesn't
drop more than three volts.
rule of thumb, branch circuit voltage has not drop more than 3% in branch wiring in a building,
5% total voltage drop from the transformer on the pole, to the plug...