Cheese said:
six-point socket II said:
Let's say you add an outlet to an existing circuit. No big deal, right?
Well, electrician #1 will tell you no problem. Does it, and when installed takes the required measurements and documents them. All said and done. Everyones happy.
That's interesting Oliver...what measurements is he taking and where is he documenting them?
Is there a central file folder on every house?
Hey [member=44099]Cheese[/member]
That is regulated by standard/code, in this case: DIN VDE 0100-600
It's applicable for newly erected, extended and modified electrical installations. It's the first thing to be done after work is completed. You basically prove that your calculations/assumptions were correct. Extensions and modifications have to be examined and it is to ensure that they are in accordance with the standards/code applicable and do not interfere with the original installation.
This is in no way complete, it should be seen as a small excerpt:
1. Inspection (To some extent this is already done while the electrical installation is erected, extended or modified. Not everything is applicable for every installation.)
- Protection against electrical shock. (Are all covers installed, no exposed wires, (...)
- Protection against thermal impacts.
- Protection against fire and spreading of fire. (Fire proof doors, fire proof maintenance/inspection flaps, (...))
- Were the correct cables, wires, bus bars, (...) used in accordance with expected loads and line voltage drop.
- Were the correct safety devices chosen and installed, were they adjusted/configured correctly.
- Were the correct appliances chosen and installed. (Think IP ratings.)
- Is the electrical installation labeled properly and entirely (wires, breakers, (...).
- Is the technical documentation of components and wiring diagram present and correct/complete.
- Are all connections properly made.
2. Test and measure. (Again, not everything is applicable for every electrical installation.)
- Continuity of ground wire, protective-equipotential bonding. If applicable secondary protective-equipotential bonding.
- Insulation resistance/ leakage resistance.
- Separation of circuits. (SELV safety extra-low voltage; PELV protective extra-low-voltage; protective separation.)
- Resistance of insulated flooring and walls.
- Protection through automated shut off. (Think fuses, breakers, GFCI, (...)) Depending on which system/ on what devices are used, there are different measurements to be taken, like loop impedance for example. If GFCI/RCD are used, those have to be tested, and loop impedance may be proven by calculation.
- Effectivity of additional safety measures/devices.
- Grounding resistance.
- Polarity.
- Correct rotating/rotary field direction.
- Check that everything works as intended
- Check/measure max. allowed line voltage drop
3. Document it.
You can buy pre-made forms to document this, or you can make your own - which might help if you have different type customers with different electrical installations. As not everything is always applicable.
The electrician will keep one set of documents for himself (think liability) and one is handed over to the owner of the electrical installation or whomever keeps these for a (building) project.
Thats the best case scenario obviously. If you ask 10 people if they can provide this documentation, 0.25 will be able to hand you something.
As you probably know: Fluke, GMW, CA ... They all make testers for this to streamline the process. Then there is a similar procedure for testing and ensuring safe use of commercially used machinery, appliances, tools, (think electrical equipment). If you work commercially in Germany you are required to have your electrical equipment/electrically operated machines (tools!) tested and documented.
If you set up metal scaffolding commercially, it has to be tested for electrical safety as well. (Think grounding)
The depth of documentation and use of testers will vary.
--
The most pleasant surprise I had in this regard, was the tech guy that put a new water distribution panel inside the soap compartment of our washing machine, that was under warranty - so no DIY.

Even though he barely unscrewed the top of the washing machine, after he was finished, he pulled out an electrical appliances tester, tested and documented it.
You remember that "cycled to death" actuator? This is what happens because many, many, many electricians do not test & measure their work. I never got any documentation/ prove of tests for that master bathroom electrical work. Neither when they moved the terminal from ground level to basement. (But back then, I didn't even know it was good practice/ according to standard/code to do this.)
And that's the next problem. Who knows this? Most employees in larger companies will know that when they bring their personal coffee maker, charging device or whatever, they should send a notice to maintenance and they will test it, and put a little sticker on it that says tested and when the next test should be performed. As they are reminded to do it by e-mail or during "work safety/accident prevention class" hold by the appointed occupational health and safety "officer"/appointee once a year.
But they have no idea that after a remodel, electrical work in their home, there should be tests being done as well.
I can't speak of the landlord perspective. I do think that landlords are required to keep this kind of documentation and have the tests done after one renter moves out and another in.
But as a home owner. I don't think there are any requirements. At least I haven't heard of it. And as a frugal home owner, who is going to ask for this extensive and pricy testing. Many electricians will go with their gut feeling and tell you: "I put in a new outlet, with new wire, why should the ground wire be broken/ where is the need to test it - if "it works" and has worked."
A different story is the underground garage complex, as it has an appointed administrator - and they, for liability reasons, keep documentation.
But obviously, these tests don't lie. And what has been tested, can't be untested. (That's majority's thinking!) So with so many electrical installations being 30, 40, 50 years old and protected if they were up to standard/code once and are not altered/extended/modified or if there is a major change in/of use. Frugal people "in the know" don't touch this subject for a reason.
And it's starting much earlier, how many people really test their GFCI/RCD - at least by pushing that little test button?
In the end, there are not many accidents/death involving electricity so I guess with common sense and the way it currently goes in the real world - "it's ok".
Kind regards,