Cheese
Member
That's exactly what I was referring to in my earlier post. It appeared to me that those wires I pointed out were 14 AWG & 12 AWG. However, by looking at and comparing their diameters relative to each other, they now appear to be 12 AWG & 10 AWG but 10 AWG wire is only NEC ampacity rated at 30 Amps and a 40 Amp breaker requires 8 AWG wire. As Tom & Ron noted, a 50 Amp circuit requires 6 AWG wire.It also appears that you have a 40 amp 240 breaker that feeds with 12 gauge wire if you actually need 40 amps that requires 8 gauge. If you don’t need 40 amps then change the breaker. It looks like a 20 amp outlet. 10 gauge wire might be better choice