Electric Trim said:
TJ Cornish said:
That's a nice idea. My crystal ball says you will eventually be switching to metal coverplates due to frequent breakage of the plastic ones. If you make a new version someday, you may want to think about putting a GFCI in as your first outlet (maybe you already did but don't have a picture), and putting in metal boxes and conduit instead of romex may make the inspectors a little happier.
Thanks for the input.
I do need to get some more durable cover plates. I have "unbreakable" plates, but they're not so unbreakable...
Do you think I should use conduit even though it's concealed behind 1/2" plywood?
yes. use 1/2" EMT. you can use metal or steel flex, or type MC cable as well, but it
would look sucky in comparison to EMT.
metal 4SD junction boxes.
raised industrial two gang
decora covers.
stranded #12 wire for hookup.
a GFCI on the first device.
you can run six other devices downstream.
for the field connection cord, use type
SO 12-3 (very important) cord, with a
heavy duty cord cap, either twist lock
or U ground, depending on your preference.
here is why:
if you are on a commercial job, and have the
misfortune to have an OSHA inspector show
up on the job, the fine for "improvised job
extension cords" is VERY expensive.
in excess of US $1,000. not exceeding $2,500.
if you do it with what i described above,
you are UL approved. you are making
an assembly from components that are
all UL listed, so the assembly is therefore
UL listed.
no fine.
(ok, i cheated. i'm an electrical contractor.
that is why i know all this off the top of my
head....)
btw... nice saw station.... ;-)
EDIT:
while plastic boxes and romex are UL listed, they aren't
listed for temporary power cord duty.....
SO cord is listed for 600 volt duty, and has a thicker
cover than SJO cord, so it won't get damaged as easily.
as far as osha is concerned, you can't even put a repair
plug on the end of a cord that came with molded ends on it.
the osha inspectors cut up cords they find like that, after
they write you a citation......
just sayin....