lloydh said:
Paul_HKI said:
OF2200 and a Midi combo is what justified picking up a second one in my case. Absolutely no issues at all, at least in Europe.
I was really pleased to see this and expected the UK model to be the same (at least the 240V I'm interested in) so why does Festool UK list the "Max. appliance socket connected load" as 1610 W, when Festool DE shows 2200 W [sad]
To understand the limitation imposed by your location in the UK, apply Ohm's law.
The Midi power rating varies from 350-1200W. Take the upper. Add 2200W for power take off for the EU market gives 3400W. Divide that by the nominal voltage, say 220V (pick the lower end of the 220-240V
nominal range in this case for the correct safety margin), gives the Ampere rating.
That example works out at 14.78 amps. On a UK 3 pin 13A plug and socket combination, that could be a bad thing, if the supply wiring to the socket were not adequately sized and protected. Not only in theory but in practice, a fire in a wall or ceiling cavity could be the end result.
On the UK market CT's, the manufacturer of ANY power tools need to consider the limitation imposed by a 13A as opposed to 16A rated plug/socket. Therefore, running the same calculation for the UK works out at 12.78A taking the 1200W for the CT and 1610W for the power take off, at 220V.
Suffice to say, the limitation in this case is all down to the UK plug and socket. A bigger CT won't help.
In order to safely power a 2200W power tool in the UK via the PTO socket on the 1200W CT, even one imported from the continent with a Schuko plug, one would need to have a rock solid 16A protected feed from a suitable bus bar in the consumer unit, feeding a 16A rated socket, into which a 16A rated plug would fit to feed the CT with its go-go juice.
Again, no suggestion you should modify a UK market CT. Just explaining what's different about your current setup compared to your European brethren. Were I to move 'home' and fit a 13A plug to my CT, a reasonable and common enough thing to do, I'd have to reduce my PTO connected power tool to something with no more than 1610W power rating to maintain that .22A margin. Unless I had a 16A Schuko socket, 2.5mm2 cabling and a suitable trip on the CU so it was being fed the same way it would have been here in the euro-norm-land.