derekcohen said:
...
I have asked about surge protectors and told that they are unnecessary in Perth since surge protection is built-in at the main box.
...
This is BOTH true and false. See below.
Either way you want to talk to a certified electrical engineer
designing home installs - i.e. the guy who does the design, NOT the one doing the installs.
Even those engineers often do not have the proper know-how in these matters and "go by the book" without trully understanding the physics at play. The surge protection "game" is closely related to lightning protection which is almost "magic" to anyone without an electrical engineering degree *and* being smart at that. Yes, I studied that and can reliably say 50%+ of the gals who exit with a degree do not -truly- understand the Maxwellian physics involved.
AstroKeith said:
Inline (ie inserted at the wall plug) protectors are unlikely to have very high capacity.
Good points. To put it "simple" for non-physicists:
For a proper surge protection, a grid-connected home needs to have - in practice - (at least) three levels. If one does not have the first two (at the breaker box), installing just the socket one is kinda placebo effect as there is no chance in h.e.ll it could handle the real surges when they come .. and the small ones it can handle are unlikely to damage (much). It certainly cannot hurt, but without the main protectors at the breaker box - which go into the tens even hundreds of kilo-
JoulesAmpers*) capacity - it has a low chance to really help.
If one *does* have a proper surge protection at the breaker box (and that usually means a *working* lightining rod on the roof etc. etc.), the last level of protection is very much desirable though - precisely to protect the sensitive electronics - the "big" level 1 or 2 protectors are not as "fast" so while they can handle the main surge, one needs a "weak but sensitive" piece at the equipment end as well.
All that said, surge protectors do *not* protect against overvoltage - say a few-second 400V on a 230V circuit - which can easily fry the semiconductor-based power supplies attached to the electronics control boards. Is important to distinguish the two.
We had a bunch of stuff go poof like this in our community shop when the ground (and thus N) on the 3-phase supply was lost and we got a "floating" neutral with 290V on one of the phases ... thankfully this was easy to diagnose. Unlike a short-but-not-surge-fast spike.
Edit:
Not sure what the FOG has against the underground, but it keeps replacing h.e,l.l with "heck" for some reason.
*) The over-current devices at breaker boxes are rated not on total accepted charge but on how fast they can dissipate it into the ground as that is ther mode of operation and also why they do not "catch" the initial spikes.