220 Electrical Question

cperren

Member
Joined
Feb 1, 2014
Messages
146
Most of my shop tools are 5 horsepower and run on a 220/30 amp circuit.  Although I do have a few 220/20 amp outlets that I'm thinking of converting to 30 amps...  All of the shop wiring is 10/4 AWG so it would be just an outlet and breaker changout... But my only concern is the power feeder for my shaper which is the only tool that is plug into a 220/20 amp outlet .. Is there any harm or concern with converting the power feeder to use a 220/30 amp circuit?  Thanks Chris

btw - the power feeder is 1 horsepower 220 volts at 6.2 amps   
 
You’ll get some disagreement on the topic, but I say it’s fine.  The circuit breaker exists for one purpose, to protect the wiring from too much current which would raise its temperature beyond a level that it was designed for (=fire).  If an appliance or motor had some other need for protection, it would have its own fuse, but that’s not the circuit breaker’s job.
 
I'll agree that if your wiring and infrastucture is up to the task then plugging a lessor power needy tool into a circuit designed for the voltage would be ok.

By example, most of the circuits in my house are 120 / 15 amp and plugging in my cell phone charger is ok.

Peter
 
The voyage is essentially constant from an outlet.  The amps is variable and depends on what the devices plugged into the outlets “pulls” or “draws”.

Any 120v tool is fine in a 120v outlet that is rated for 15amp or 20amp.

 
As everyone else said, no problem or harm converting the power feeder outlet to 30 Amp.  But is there really any need to do it?  Power feeders generally are fixed in place and you almost never ever move them around the shop.  You will likely never ever plug the power feeder into any outlet other than the one its already plugged into near the shaper.  I suppose you could move the power feeder over to the table saw and use it there.  Do you already have another power feeder at the table saw?  But if you do that, I'd just suggest running a wire from the current plug over to the saw and putting a 20 Amp outlet there using the exact same breaker.
 
Yep, I usually use the same outlets with respect to the shaper and feeder although they are mobile... Its more about just standardizing to one outlet type throughout my shop...  Thanks 
 

Attachments

  • IMG_0392.jpg
    IMG_0392.jpg
    2.4 MB · Views: 595
As stated by [member=21249]RKA[/member] the breaker is meant to protect the wire. A fault in the circuit between the machine and the outlet could cause the wire to melt or catch fire. The odds of it happening are low as the machine probably has internal overload protection and any short will most likely trip the breaker. 

That being said, I've decided not to go this route in my shop. 20A machines are on a 20A circuit. I was thinking of using higher gauge wire in the walls to have the option of upgrading the circuit size down the road but that would lead to mixed machines so if I ever need more, I'll just run a new circuit.

I'm not an electrician, one might say that it's fine, I'm just playing it safe.
 
**DISCLAIMER** Always check your local electrical code

-Do both power tools fed from the same breaker? If no, there is no problem
-If both power tools are on the same 30 amps: check the rate (not peak) of each tool. If your shaper draw 22amps and your power feeder draw 16amps your breaker will suffer from fatigue and at one point will trip.

I am not familiar with  power feeder but I believe you can tweak the feed rate/pressure which may change the consumption. For example if your power feeder is set to apply a maximum of pressure on the lumber and you feed the shaper with hard wood like Wenge, the total consumption will increase. You can go a bit over 30amps but it's at your own risk  [eek] eventually the breaker will trip. Your power tools should not get damaged tho.

Note: Personally when a breaker has tripped more then 5 times I ditch it
 
MCCBs (Molded Case Circuit Breakers) are all over the place with their trip points. If you had the capability to test them you'd see that. Where I worked (power plant) ALL MCCBs got tested before installation. For those that were adjustable (single or dual pole @
 