jaguar36 said:
Something else going on there, no reason Festool vacs or other tools using brushed motors in good condition should be tripping a dual fault breaker. Either the Festool is in poor shape and has a broken conductor arcing very badly, or there is a wiring or breaker issue. The Arc Fault portion of the 'Dual' function breaker should not trip based on the small arcs that occur in brushed motors (or switches and plugs).
Almost all kitchen appliances are brushed motors as well.
A more likely problem is the breaker not working (properly) on the ground fault side. "Older" standard GFCI breakers were 30mA while the new "dual ones" seem to have gone > 5 mA. I.e. 6x more sensitive than before.
Even with the 30 mA ones standard, there were devices which needed a 300 mA breaker to be used instead.
With the high-powered full-wave electronic motor control units there can be small (way beyond safe) capacitive current transients seen on the ground wires. If the GFCI part of the breaker is too sensitive - in this case a bad design/cheap one will be the more "sensitive" one - it may trip under an otherwise normal within-spec operation.
Most kitchen appliances *) are not grounded these days, hence the GFCI "issue" would not be observed. Same for most home vacs.
*) meaning hand-use ones