Was me ... fixed, thanks! Was some time I dig into this and memory is not as it should be ...Coen said:Btw someone commented on 3-phase above being 60° apart; it's 120°
Was me ... fixed, thanks! Was some time I dig into this and memory is not as it should be ...Coen said:Btw someone commented on 3-phase above being 60° apart; it's 120°
Bob D. said:gunnyr said:Me thinks its all about the money [wink] [wink]..... At the volume a company like Festool operates on, saving even $0.20 per item adds up to big bucks.
I've mostly relegated the 16ga cords to the bottom shelf in the back of my shop. Like others I've trimmed the tab off one or two cords....
I think any perceived savings is offset by additional costs of having to maintain near duplicate items in inventory and all the other duplication associated with the two items. In the warehouse you have to create a unique space to stock each cord that are nearly identical and difficult to tell apart by eye without close inspection.
And then you create the aggregation for users with two cords.
It would be easier on all just to have the one cord rated for all Plug-It tools. And it would cost nothing to make the change, just include the 16Ga cord from here on out, and let the 18Ga cord fade away.
Coen said:Really? Everything in households is regular 16A Schuko and for the cooktop we have 3-phase, using same cross section wiring for 11,1 kW. Usually 1 per home. Or empty conduit in case the cooktop uses gas.
And even things like computer powersupplies run more efficient on 230V
Coen said:DeformedTree said:For the big tools like the OF2200, Festool could have given it a 20A plug.
It doesn't? It has a 15A plug? So the US gets a nerfed OF2200? OF1650?
Coen said:The safety thing is taken care of by reduced risk of fire from currents half as big and partly insulated plugpins. Likelyhoid of getting zapped with 230V is enormously reduced. Use savings in copper for full coverage with 30mA RCD's. These stories of people zapping themselves by disconnecting their phonecharger are something US-only with the bare pins. Impossible with the europlug.
And that you guys in de US don't particularly seem to limit energy use is known yeah :+
Coen said:Vacuum cleaner, oven, hair dryer, paint stripper, OF2200, washing machine, water kettle; all items that usually are 10A at 230V and are connected to a regular socket here.
DeformedTree said:Coen said:Really? Everything in households is regular 16A Schuko and for the cooktop we have 3-phase, using same cross section wiring for 11,1 kW. Usually 1 per home. Or empty conduit in case the cooktop uses gas.
And even things like computer powersupplies run more efficient on 230V
Everything in a household runs off a 15Amp plug here, just like you have a 16A plug for everything. The other plugs are used for locations you don't have plugs.
DeformedTree said:Computers convert it to low voltage DC, nothing changes. The efficiency loss is in the AC to DC conversion.
DeformedTree said:Coen said:DeformedTree said:For the big tools like the OF2200, Festool could have given it a 20A plug.
It doesn't? It has a 15A plug? So the US gets a nerfed OF2200? OF1650?
No, it's an OF2200, running full power is very rare, and even if it does, it would be a short period of time. You can pull more than 15As on a circuit for a while before the breaker kicks. Users of OF2200 don't report issues.
DeformedTree said:Coen said:The safety thing is taken care of by reduced risk of fire from currents half as big and partly insulated plugpins. Likelyhoid of getting zapped with 230V is enormously reduced. Use savings in copper for full coverage with 30mA RCD's. These stories of people zapping themselves by disconnecting their phonecharger are something US-only with the bare pins. Impossible with the europlug.
And that you guys in de US don't particularly seem to limit energy use is known yeah :+
Reducing currents doesn't change the safety. The wire is correctly sized, there is no increased chance of fire because more amps are involved. Increased voltage is the safety issue. Who is zapping themselves with their phone charger? The only folks who get zapped are kids jamming stuff in outlets, and thus why we have tamper resistant outlets. I've never zapped myself just plugging/unplugging something. When you go higher voltage, you have to take more steps for safety.
DeformedTree said:I have nothing wrong with 230V power, and 3 phase setups, I like them. I have stuff wired for 240V, and own 240V tools, plenty of us have this. But you have this false idea that the North American power system is a mess, or bad. It's not. It's just different, but it works very well. Europe is going to have issues dealing with going all electric. Folks can try tuning it out, but gas cars, gas usage in homes is going away. The US is all set for this, most home can already handle going full electric. The infrastructure is there.
DeformedTree said:I'm trying to find a spec on what wire is used in the walls over there.
DeformedTree said:Looks like 1.5mm^2 and a 70C temp rating, having found the voltage rating. That is wire that is about 16gauge US. We don't use that small, you need 14gauge for just 15A and your temp rating is very low, so you would need even bigger. The NEC doesn't even have any ratings for 16 gauge and temp ratings that low. Would like to see a link to something showing the spec for structural wiring over there (gauge, temp, voltage ratings).
Cheese said:Coen said:Vacuum cleaner, oven, hair dryer, paint stripper, OF2200, washing machine, water kettle; all items that usually are 10A at 230V and are connected to a regular socket here.
That's interesting...our oven/range is 40A/240V and the dryer is 30A/240V.
Not really.DeformedTree said:Your wiring sounds complicated.
DeformedTree said:For the big tools like the OF2200, Festool could have given it a 20A plug.
It doesn't? It has a 15A plug? So the US gets a nerfed OF2200? OF1650?
mino said:Not really.DeformedTree said:Your wiring sounds complicated.
For home use, you basically have 2 "gauges" as you would say in the US: (but we use millimeters)
- 1,5 mm2 for the occasional low-current fixed installations (basically lights only)
- 2.5 mm2 for any installations where sockets are installed (as these are 16A by default)
Now, as mentioned, the real technical property of an installation is impedance (to ensure breaker reaction) and temperature generation.
In Europe, we mostly have brick or concrete houses, so heat generation is a moot point: Like totally moot as a wire embedded in concrete or plaster has a very good heat transfer media.
For wood/plaster houses which are rare, there is actually separate, stricter, standards for cabling as the limited heat dissipation in wood buildings is taken into account.
I can see how this can be confusing for a US based person - you standards assume a "wooden house" with all its fire risks while a typical European house would have the installation either embedded in concrete or brick wall, making the standards accommodate that as fire hazard (in the installation itself) is pretty much non-existent and only the endpoints like breaker boxes or sockets are a concern there.
Either way, any qualified electrician is primarily concerned about impedance. And that is more about distance and installation topology than cable "gauge" in practice. Second comes cable cooling/heat generation, but that is usually non-issue outside wooden houses which are rare so have a special standard.
DeformedTree said:Far as the plugs, you say it's easy, to shock yourself, yet we don't seam to shock ourselves with them. You have to actively try.
DeformedTree said:Your wiring sounds complicated.
DeformedTree said:For houses, they are almost always done with NM-B (aka romex trade name). It's a PVC sleeved cable. You can do wires in conduit as well, in some areas it's required (Chicago). We don't have to go thru harmonizing, all of north America, the Caribbean, and parts of south America use the NEC (national electric code) and it's been unchanged on the core parts forever.
DeformedTree said:Most of house is 14 gauge NM-B. Lights, plugs, etc. For circuits required to be 20A, you use 12 gauge. We also have some limited stuff such as dryers, air conditioners that are general 30A/240V, so run with 10 gauge.
DeformedTree said:A few things might go 8 gauge if 40A,
DeformedTree said:and items like stoves, ovens, etc will get 6 Gauge (55Amps).
DeformedTree said:These bigger items are almost always 240V, unless they are dual voltage 240/120V like a dryer. Same wire for all, NM-B. 90C rated, 600Volt insulation. It used to be 60C rated, so sizing wise it is still treated as 60C, even though the wire is now higher rating. It was found that heat from light bulbs, combined with increase in insulation decades ago made the 60C rating too low, so they increased it, but didn't want folks changing the wire size. You can't run NM-B in conduit, has to be individual strands, which is the same wire really. Various rules on conduit fill to prevent over heating.
DeformedTree said:Your gauge wire and it's temp rating is simply not legal. Way too unsafe/undersized.
DeformedTree said:You guys are fearing amps because your wire is undersized.
DeformedTree said:You would need to be 12 gauge in the US to do 16A with a 60C insulation (but of course 60C insulation is not legal). Our wires don't get hot when running at full amperage.
DeformedTree said:mino said:Not really.DeformedTree said:Your wiring sounds complicated.
For home use, you basically have 2 "gauges" as you would say in the US: (but we use millimeters)
- 1,5 mm2 for the occasional low-current fixed installations (basically lights only)
- 2.5 mm2 for any installations where sockets are installed (as these are 16A by default)
Now, as mentioned, the real technical property of an installation is impedance (to ensure breaker reaction) and temperature generation.
In Europe, we mostly have brick or concrete houses, so heat generation is a moot point: Like totally moot as a wire embedded in concrete or plaster has a very good heat transfer media.
For wood/plaster houses which are rare, there is actually separate, stricter, standards for cabling as the limited heat dissipation in wood buildings is taken into account.
I can see how this can be confusing for a US based person - you standards assume a "wooden house" with all its fire risks while a typical European house would have the installation either embedded in concrete or brick wall, making the standards accommodate that as fire hazard (in the installation itself) is pretty much non-existent and only the endpoints like breaker boxes or sockets are a concern there.
Either way, any qualified electrician is primarily concerned about impedance. And that is more about distance and installation topology than cable "gauge" in practice. Second comes cable cooling/heat generation, but that is usually non-issue outside wooden houses which are rare so have a special standard.
Our electrical code assumes nothing about the construction of the house. Our electrical code concerns the wiring. Sizing is based on the wire, it's insulation. We use the same code for a small basic house, garden shed as we do in a sky scrapper, an industrial plant, bomb shelter, etc. It's all NEC. Generally the residential building code cuts out stuff that doesn't apply to a house, but it's all the same. Most homes don't need to be concerned with explosion proof construction, gigawatts of power transmission, etc.
DeformedTree said:Most residential is prescriptive, thus there is a clear simple path for stuff, such as particular gauges of a particular type of wire for various applications. Just like framing, plumbing, etc in code. So folks don't have to have an engineer review the design, everyone knows it works. But you can deviate if you want, and then you get into endless tables for all types of wire made, the ampacities for different temperature ratings, when you can use what, de-rates for different applications, so on and so forth.
DeformedTree said:It's illegal to embed a wire in plaster/concrete/etc.
DeformedTree said:It must be protected in conduit if in masonry material like that. Wiring is either in conduit, or it's not. For electrical power transmission, NM-B, UF (a direct burial in dirt spec), and some SE (service entry) cable is design to be run not within conduit. Everything else is in conduit, the sizing doesn't care what is around the conduit (free air, dirt, concrete, fruit cake). Most residential wiring is not in conduit. Other than the Chicago thing, residential only tends to start going conduit in places like apartment buildings, high rises, etc. You can have a big wire in a big conduit, moving just a few amps, and the conduit is buried in the ground (55F), you can't just say "it's fine, the ground is cold".
DeformedTree said:We don't look at impedance, there is no point. We don't size our stuff so dangerously. If you have a bad connection, you will notice the lights dim, voltage drops, etc. Breakers will kick. You are either pulling too many amps for the breaker or you're not. It doesn't care what is down stream of it. It's the "weak link" not the wire.
DeformedTree said:There is only 1 topology, we don't have ring bus's or any of those problematic issues.
DeformedTree said:We have branch circuits, a limited number of items on each circuit. Length of a wire run is almost never an issue. You can only get so far from a panel in a house, and even houses with one circuit wrapping around the house several times, you don't see issues. Wires are sized to handled the amps of the circuit and stay within the temperature limits of the wire. Breakers are sized to protect the wire. If someone has some concern due to distance, they might bump up the size. As mentioned, some folks will just wire everything with 12gauge both for a level of simplicity and extra margin, you can always have a smaller breaker.
DeformedTree said:Hard to access wires later, so often best to install bigger than needed, and then just install a smaller breaker. Common for ranges, ovens, etc. Run 6 gauge so you could support 50-60A, but if someone installs a unit that only needs a 40A breaker, it just means more margin. The cost difference is pretty minimal verses the headaches later.
Bob D. said:"So your common electric water kettle is like 1600W?"
Yours probably is too.
Bob D. said:Watts is watts
1600W/120V = 13.3A
1600W/240V = 6.66A
Doesn't use any more power (watts) than a 240v kettle.
Bob D. said:One of the reasons for the difference in secondary voltages is that when the power distribution system was first developed here by Westinghouse and Tesla much of the country was still building out and space for the necessary equipment was incorporated into new construction and communities. In Europe most places were already built up and electric systems were added to existing homes and other structures. Your cities, at least what I have seen in many of them, appear to be more tightly packed, much higher population density, leaving little room for transmission and distribution equipment. A higher primary/secondary voltage helps overcome this because the power can be pushed much further down the wire from the last transformer. In NA where there was plenty of room to grow this was not necessary. That and migrating over from Edisons' inadequate DC system which was trying to scratch out a start in New York and New Jersey might have something to do with it too.