Holmz said:On a 230v unit...
No, that is not how a transformer works. Whatever is happening on the output side of a transformer appears on the input side, and that includes an open circuit. Virtually no current will flow in a transformer with no load connected.Bohdan said:A transformer without a load on it is in itself a reactive load. This means that while it is not drawing any power (watts) it is still drawing a significant current. This current is nearly 90 degrees out of phase with the voltage so there is little or no power being consumed.
Another way of putting it is to say that the power factor is close to zero. However if the CT's sensing circuitry is designed to trigger on current flow, rather than power consumed, it would see the unloaded transformer as a significant load and run the extractor.
This situation gets worse the larger the rating of the transformer so it may be possible to find a transformer that is small enough not to trigger the CT but it would not supply enough power to run the tool.
Rick Christopherson said:No, that is not how a transformer works. Whatever is happening on the output side of a transformer appears on the input side, and that includes an open circuit. Virtually no current will flow in a transformer with no load connected.
Of all the inventions man has created, the simple transformer is the closest to perfect. The real life transformer behaves very close to the mathematics of an ideal transformer. When people say their transformers draw significant current when not in use, it's probably because they aren't transformers at all, but electronic power converters. If you have a true transformer, it would not trigger a CT vac.
Bohdan said:Rick Christopherson said:No, that is not how a transformer works. Whatever is happening on the output side of a transformer appears on the input side, and that includes an open circuit. Virtually no current will flow in a transformer with no load connected.
Of all the inventions man has created, the simple transformer is the closest to perfect. The real life transformer behaves very close to the mathematics of an ideal transformer. When people say their transformers draw significant current when not in use, it's probably because they aren't transformers at all, but electronic power converters. If you have a true transformer, it would not trigger a CT vac.
If that is true then why do all of the users in Britain that plug a transformer into their CT find it running with no tool connected.
Rick Christopherson said:Bohdan said:Rick Christopherson said:No, that is not how a transformer works. Whatever is happening on the output side of a transformer appears on the input side, and that includes an open circuit. Virtually no current will flow in a transformer with no load connected.
Of all the inventions man has created, the simple transformer is the closest to perfect. The real life transformer behaves very close to the mathematics of an ideal transformer. When people say their transformers draw significant current when not in use, it's probably because they aren't transformers at all, but electronic power converters. If you have a true transformer, it would not trigger a CT vac.
If that is true then why do all of the users in Britain that plug a transformer into their CT find it running with no tool connected.
Because what they are calling a transformer is most likely an electronic power supply.
Holmz said:It alights the CT-26 every time... maybe I should get the Amp meter out?
Dainius G said:Ok, so 60W 110V bulb does not start the CT, 500W 110V halogen does. So that narrows it down to 60W-500W load requirement. This probably means that the load can be reisistive and since the least power drawing festool power tool (designed to work with CT) seems to be the Eccentric sander ETS 125 that rates @ 200W narrows it to 60W to 200W.
I guess I should have explained why am I asking about this, well while the autostart function is a nice feature, I find it inefficient for my purposes. I lay wooden floors for a living, when working my CT is connected to my mitresaw to chop the boards and then finishing trim. I work fast and I find more so then not my CT only spools up when I`m already halfway through my material(=a lot of dust). So I want to add a sensor/dummyload to my mitresaw to kick in the CT few moments early as I approach the machine, perhaps even add a few button controlled pre-set modes. I know that one day these features will be incorporated in most festool machines as the IOT progresses but for now I`d be happy with getting this Idea working [smile]
BTW my 3.3kVA 240V to 110V transformer starts (atleast what my multimeter clamp can read)(NO LOAD) with more than 15Amps and then quickly settles to about 1.3-1.4 amps which means its ~ 310-325 Watts is more than enough to start the CT.